The AC unit is 2006. Had to replaced the furnace / evaporator fan capacitor twice the last two years. Both times the fan speed was low and the evaporator coil iced up so almost no air flow from the ducts. Initially thought it was low refrigerant causing the coil icing. This year the unit is not running again but the furnace fan speed was blowing normally. Checked the condensing unit outside and the fan would hum while the compressor would click and tried to start.
.
1) Had good voltage at contactor and was working properly. Removed and sanded contacts with 600 grit to be sure.
2) Fan would spin if you helped it along with a stick or screw driver
3) Capacitor was bulging but didn't know if was a dual run unit so thought the compressor was bad.
4) The scroll compressor didn't looked like it had a capacitor built in. After watching a Youtube video realized it could be a dual run so it should be for both the compressor and condensing fan.
.
For good measure ordered a new contactor, new capacitor and a new to me hard start capacitor. To think I used to do load calcs, design walk ins, blast freezers including sourcing and putting it all together, Oxy Acetylene welding with nitrogen and all. Have a Universal CFC so turn key except for the electrical
Parts will arrive tomorrow so hopefully that it?
.
.