Yes, yes, yes and yes, lol. I'm not thinking it has anything to do with the new parts either, but an existing partial blockage or problem with the expansion valve, that only became worse after introducing a vacuum to the system. And with the AC causing the car to completely stall out points to over-pressure in my eyes.firstv70volvo wrote: ↑20 Jul 2023, 09:58So the short cycling of the compressor began when the condenser was replaced, the short cycling happened with both compressors? The receiver/drier was replaced at the same time too? Was the pressure switch from the old receiver/drier transferred to the new receiver/drier, was the wiring harness connector plugged in correctly to the sensor? I'm having a hard time thinking the new parts have a blockage so am questioning the installation of the new parts and something may have been done incorrectly. It's not out the question there could be something could be wrong with the condenser or receiver/drier but this seems less probable to me.soulvoid21 wrote: ↑20 Jul 2023, 09:20Dryer was replaced as part of the condenser, it came with the replacement.firstv70volvo wrote: ↑20 Jul 2023, 08:02
From what I can tell you have had a refrigerant charge of 700kg, 1000kg and 1300kg in the system. The dealer said it needs 1000g based on your VIN. If the compressor is short cycling at both 700kg and 1000kg charge levels there's another problem other than the charge. If the system pressure is too low or too high the compressor will be commanded to shut off, the pressure switch is on the receiver/drier. What are the gauge readings saying?
If the pressure sensor is working correctly and there's is a blockage in the system, I would expect you to see have a very high pressure reading on the high side gauge and a lower than expected reading on the low side gauge. Another indication of a blockage is the gauge readings after the running the compressor and watching how long it take for the low and high gauges to equalize after shutting off the engine. It shouldn't take more than a few minutes for these gauges to equalize. When you replaced the condenser was the receiver/drier also replaced? When your mechanic has the system apart for flushing it should be easy to determine if there's any blockage in the condenser, evaporator or hoses. You can't flush the expansion valve or receiver/drier but you should check these for blockage with some compressed air with these components. Because you've replaced the condenser and will be replacing the expansion valve you should pay special attention to the receiver/drier if this has not been replaced, this will be a likely area for blockage. Check the old expansion valve with air too, at room temp air should flow freely through it.
Did the short cycling begin with the new compressor?
Short cycling started after changing the condenser first. Cycling continued with the new compressor.
Idea to check for blockage is exactly as you said. Tear it down and try with compressed air on the parts possible. Just changing the expansion valve regardless because it’s cheap/easy enough, and one less thing for me to worry about later on.
I don’t know the pressure readings yet. They vacuumed the system in preparation to tear it down to check for blockages. So I guess that’s our next step. If we don’t find any and continue to have issues, I’ll get exact pressure readings during multiple scenarios.
Just waiting at this point for him to check for blockages/attempt to flush the system. Thankfully, I'm not in a huge rush as I have a beater Jeep Liberty I can drive for the time. Once he completes the flush, or attempts it, I'm sure we'll have more information to go on.